I have a situation where we are installing a genset to serve an exisiting building. Our plan is to interupt the service conduits running into the building and route this normal power into a Pad Mounted Service Rated NEMA 3R Automatin Transfer Switch located next to the proposed Genset.
My question is... Do I need a disconnect means to be installed ahead of the transfer switch now because it is ahead of my Service equipment (Main Panelboard) that is located in the building?
The neutral that is derived from Genset, and the neutral coming from the 4-wire service will meet in the ATS. Do I tie these neutrals together, or do I need a need a 4 Pole ATS that isolates the individual neutrals?