JDBrown
Senior Member
- Location
- California
- Occupation
- Electrical Engineer
The issue of providing a proper disconnecting means for an outbuilding has come up a few times recently, and I find that, the more I look into the Code requirements, the less confident I am in my understanding of all the related nuances.
My latest confusion is regarding NEC 225.38(C), which says:
Now, I can't think of any reason why I would want to do it that way -- to the contrary, it sounds like a very bad idea to me -- but it appears that it would be Code legal. Is this correct, or have I been staring at the NEC for so long that I'm seeing things that aren't there?
My latest confusion is regarding NEC 225.38(C), which says:
So, a means has to be provided for disconnecting the grounded conductor (e.g. the neutral). This seemed a bit odd to me at first, because why would you want to open your neutral? This section seems to allow me to switch the neutral (say, by using a 4 pole switch on a 3 phase, 4 wire feeder or MWBC), but if I don't switch the neutral with the phase conductors I have to provide another means of disconnecting it. Based on the wording of 225.38(C), it seems that the neutral lug on a standard disconnect switch would qualify. But since it doesn't require the grounded conductor to be disconnected simultaneously with the ungrounded conductors, it also sounds like I could bring my feeder into an enclosure with two switches, one which would disconnect the ungrounded conductors and the other which would disconnect the grounded conductor.(C) Disconnection of Grounded Conductor. Where the building or structure disconnecting means does not disconnect the grounded conductor from the grounded conductors in the building or structure wiring, other means shall be provided for this purpose at the location of disconnecting means. A terminal or bus to which all grounded conductors can be attached by means of pressure connectors shall be permitted for this purpose.
Now, I can't think of any reason why I would want to do it that way -- to the contrary, it sounds like a very bad idea to me -- but it appears that it would be Code legal. Is this correct, or have I been staring at the NEC for so long that I'm seeing things that aren't there?