disconnecting means from building

Status
Not open for further replies.

gserve

Senior Member
Location
New Hampshire
Is there a requirement in the code like in article 550 that addresses a maximum distance from the building to have a disconnect? I would like to have a pole mounted service and then feed the building which is 200' away there will be a main breaker in the panel closet to the point of entrance inside the building. Basically service on pole and feeder to building, service at building treated as sub-panel with isolated neutral,4 wire and also a GES. Or in other words how far can the service disconnecting means be from the building
 

jwelectric

Senior Member
Location
North Carolina
Re: disconnecting means from building

Could this building fall under the scope of ARTICLE 547 Agricultural Buildings?

:)

[ September 29, 2005, 09:10 PM: Message edited by: jwelectric ]
 

websparky

Senior Member
Location
Cleveland, Ohio
Re: disconnecting means from building

You are confussing two different things. One is the "Service Disconnect" and the second is a "disconnecting means suitable for service equipment".
In your scenario, there is no limit to the distance of the feeder. Of cource, all other code requirements still need to be considered once the feeder reaches the second "structure".
 