- Location
- Lockport, IL
- Occupation
- Semi-Retired Electrical Engineer
I?m designing a facility that will have a diesel generator as a back up source. There will be an ATS for ?Life Safety? loads (egress lights), and a separate ATS for ?Optional Standby? loads. 230.2(A)(2) and (4) allow me to use this DG as a second service (in my case, second and third service) to the building. The specifications for the DG set will require two, separate, local disconnecting means. They will be accessible, and within sight of the building. Per 700.12(B)(6), I don?t plan on placing another pair of disconnects at the point at which the DG?s conductors enter the building. Two questions:
</font>
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Are the two local disconnects at the DG required to be ?Service Entrance Rated??</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Is it unusual to require the DG vendors to provide ?Service Entrance Rated? local disconnects (i.e., is this not their standard product)?</font>