Question on Prep Exam
Example test Question. When an inverse time circuit breaker is used as a disconnecting means only for a 7.5 HP Single phase 240v ac motor the CB must have a standard amperage rating of at least?
My answer is 50amps
7.5 hp fla =40a table 430.248
40a x 115% = 46a next highest 50a
SO you size disconnect by 115% per 430.110 separate from MCP for motor than can be adjusted for higher settings if needed ? I am just wondering if the disconnect breaker would trip before the mcp if sized this way. I always assuned you used 430.52 to size OCP.
My answer is 50amps