Disconnecting meens
New member
When installing a new or replacing an existing service. Does NEC require a disconnect at the meter location if the meter is more than 10 feet away from the main panel. I have always done it this way but now I'm being told there is no 10 foot rule. Is this true?
Thanks Mike
Re: Disconnecting meens
What would the purpose of this disconnect be?
My house has a meter on the outside and the panelboard inside. No disconnect outside. Its probably within 10 feet.
That is false. If you have to cross a stud space or floor space you must have a disconnect. Also, I believe it is 6 feet on the disconnect. Either way, you will need a disconnecting means at 10 feet for sure. Regardless of the situation, think about it, that run of wire is not fused. Do you want a piece of wire running across your home unfused. Negative. If the meter is not behind the panel or if the meter is not within 6 feet below leading into the basement where the panel is placed, I put a diconnect. Its smart, safer, and code.
There is no 10 foot rule, or 6 foot rule in the NEC.
There is an errata in the 1st printing of the 2002 NEC in section 338.10(B)(4), the 3rd paragraph that states "The length of the cable extending indoors to the first termination box shall not exceed 6 feet."
I believe this is where alot of the confusion stems from.
230.70(A)(1)
"...either outside of a building or structure or inside nearest the point of entrance..."
There are some jurisdictions that override the NEC and permit the Service Entrance Conductors to be installed further inside a building than permitted by the NEC.
[ February 24, 2005, 06:39 PM: Message edited by: pierre ]
If the service entrance conductors are under or behind 2" of concrete or brick, they are considered outside the building. You can run them as far before hitting a disconnect as you want if they are outside.
"Nearest the point of entrance" is a judgment call by the AHJ. Most will let a conduit come up through a floor and run 2 or 3 feet to panel height before hitting overcurrent protection.
Steve
Steve