horses
Member
- Location
- Bradenton, Florida
I have a 75 kva transformer that is located between 20-25 feet from either the panel that is feeding the primary side & the panel that is being fed on the secondary side. The panel on the secondary side has 225A main breaker panelboard on the secondary side. The primary side is being fed from a 3P 90A breaker.
The transformer is not in the same room, it is on the other side of a wall. The engineer did not show an actual disconnect on next to the transformer. I feel as if the transformer needs a disconnect within site of it on both the primary & secondary sides.
I dont see anywhere in 450-3 where they call out an exact location requirement for either the primary or the secondary. Any help will be greatly appreciated.
The transformer is not in the same room, it is on the other side of a wall. The engineer did not show an actual disconnect on next to the transformer. I feel as if the transformer needs a disconnect within site of it on both the primary & secondary sides.
I dont see anywhere in 450-3 where they call out an exact location requirement for either the primary or the secondary. Any help will be greatly appreciated.