dwellins
Member
- Location
- Punta Gorda, FL
Wondering if it is legal to install (2) 40 amp Disconnects (for 2-package AC units -22 RLA 40A max OCPD) from the secondary side of a 45KVA transformer. Transformer will have primary OCPD (125%). Transformer will be located outdoors with disconnects mounted approximately 15' from transformer. Disconnects will be grouped. I will have (2) conduits & conductors (#8 AWG CU) leaving the transformer until they reach the (2) disconnects which then will supply the AC units.
This will be the only 2 items fed from the transformer
FYI this will be step-up transformer from 240 Delta to 480/277---The engineer spec'd and ordered wrong AC equipment so it is falling in our hands to resolve it. :slaphead:
Original plan was for a panelboard with a 70 A Main with 2-40 amp OCPD for equipment but they are trying to save some $$
Thanks for any input
This will be the only 2 items fed from the transformer
FYI this will be step-up transformer from 240 Delta to 480/277---The engineer spec'd and ordered wrong AC equipment so it is falling in our hands to resolve it. :slaphead:
Original plan was for a panelboard with a 70 A Main with 2-40 amp OCPD for equipment but they are trying to save some $$
Thanks for any input