do disconnects that are not fused need arc flash warnings does that depend on the voltage and amps
 

dkidd

Senior Member
Location
here
Occupation
PE
It depends on whether the AJU considers they

"are likely to require examination, adjustment, servicing, or maintenance
while energized"
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Depends.. will it be “examined, adjusted, serviced, or maintained while energized,”

Edit: beat me to it...
 

mwm1752

Senior Member
Location
Aspen, Colo
Why would you likely to require to have a non fused disconnect energized for examination, adjustment, servicing, or maintenance ? It is either on with power passing thru or the OCPD serving it is off -
 

mwm1752

Senior Member
Location
Aspen, Colo
Testing voltage to an HVAC unit. You could accidently short it.
if the switch is closed then voltage if it exists would go to HVAC - you could test for voltage at the HVAC as well - If the HVAC does not have voltage then if you open the disconnect is would not have voltage as well. Would you need clearances for a wall switch? it can be considered a non fused disconnect in certain uses. Likely is the term used
 