Hello,
I am inquiring about clearance requirements for disconnect switches. I have several dorm rooms each with a 12 square foot mechanical space. In this mechanical space I have a heating cooling HVAC unit that requires 2 dedicated circuits.
CKT #1 44 MCA
CKT #2 21 MCA
I need to place the disconnects in this room. The ductwork above covers most of the room.
I believe I meet the requirement of 110.26(e). I do not believe I need to meet the requirement of 110.26(f).
If I have ductwork above these disconnects is this a code violation, I believe the answer to be no.