We are trying to get a handle on the type of fire alarm system we have installed now from 1975 so that we can describe the scope of work accurately for the contractors in order to upgrade.
The present fire alarm panel we have now in our facility is outdated and can not get parts for it. There is long rectangular junction box that feeds two conduits to the fire panel not considering the conduit coming from the back-up battery that also enters the fire panel. That makes a total of 3 conduits that actually interface with fire panel itself. Entering the long rectangular junction box is a conduit from the electrical power subpanel and 13 other conduits coming from the ceiling. That means one conduit only enters the fire panel that is for signaling (in order to feed the initiation and notification devices) in my estimation since the other two conduits are for power and back-up power.
Our drawings from the building do not show whether it is a conventional, addressable, class A or class B system. We figure from the description above it could be any one of these configurations. Do you agree?
There are 15 small red boxes located near the fire panel and I assume these to be shut down initiating device boxes for the shutdown circuits or possible relays.
The existing fire panel drawings show 4 wires emanating from the panel per circuit for a total of 3 zones. It should be 2 wires per circuit in my estimation for a conventional or addressable system (although only 1 circuit is required for addressable). This leads me to believe the extra two wires are for the relays or what could be shutdown circuits. Or it is a possibility that the other 2 wires are to make the system addressable with the outgoing and incomming circuits sharing the same conduit interfacting with the fire alarm panel. Would you have an idea?
Also can I install an addressable, Class A fire alarm distribution circuit with shutdown circuits emanating from the fire panel with only a 2 wire system? I don?t want the shutdown circuits being located external to the fire panel, but actually part of the software resident in the fire panel.
I also want to make sure the fault isolation monitors I am installing will not require extra cabling back to the fire panel. Do you know?
The present fire alarm panel we have now in our facility is outdated and can not get parts for it. There is long rectangular junction box that feeds two conduits to the fire panel not considering the conduit coming from the back-up battery that also enters the fire panel. That makes a total of 3 conduits that actually interface with fire panel itself. Entering the long rectangular junction box is a conduit from the electrical power subpanel and 13 other conduits coming from the ceiling. That means one conduit only enters the fire panel that is for signaling (in order to feed the initiation and notification devices) in my estimation since the other two conduits are for power and back-up power.
Our drawings from the building do not show whether it is a conventional, addressable, class A or class B system. We figure from the description above it could be any one of these configurations. Do you agree?
There are 15 small red boxes located near the fire panel and I assume these to be shut down initiating device boxes for the shutdown circuits or possible relays.
The existing fire panel drawings show 4 wires emanating from the panel per circuit for a total of 3 zones. It should be 2 wires per circuit in my estimation for a conventional or addressable system (although only 1 circuit is required for addressable). This leads me to believe the extra two wires are for the relays or what could be shutdown circuits. Or it is a possibility that the other 2 wires are to make the system addressable with the outgoing and incomming circuits sharing the same conduit interfacting with the fire alarm panel. Would you have an idea?
Also can I install an addressable, Class A fire alarm distribution circuit with shutdown circuits emanating from the fire panel with only a 2 wire system? I don?t want the shutdown circuits being located external to the fire panel, but actually part of the software resident in the fire panel.
I also want to make sure the fault isolation monitors I am installing will not require extra cabling back to the fire panel. Do you know?