Disecting article 300.5(I) of the NEC

Status
Not open for further replies.
...what does the term 'isolated phase' mean?

Lets not play around, lets get to the point. :)

Your opinion is that exception 2 to section 300.3(I) ...

Exception No. 2: Isolated phase, polarity, grounded conductor, and equipment grounding and bonding conductor installations shall be permitted in nonmetallic raceways or cables with a nonmetallic covering or nonmagnetic sheath in close proximity where conductors are paralleled as permitted in 310.10(H), and where the conditions of 300.20(B)

... if used requires each phase, grounded and grounding conductor to be run in sperate conduits.

It is my opinion that the section does not require that and that we may run A&B in one conduit and C&N in another conduit using that exception.
 
Here is the the main section

300.5 Underground Installations.

(I) Conductors of the Same Circuit.
All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors shall be installed in the same raceway or cable or shall be installed in close proximity in the same trench.

Exception No. 2: Isolated phase, polarity, grounded conductor, and equipment grounding and bonding conductor installations shall be permitted in nonmetallic raceways or cables with a nonmetallic covering or nonmagnetic sheath in close proximity where conductors are paralleled as permitted in 310.10(H), and where the conditions of 300.20(B)
 
The question is a good one as the term "isolated phase" is not defined in the NEC. I can see it being read as one phase per raceway and not including more than one phase per raceway.

I don't even know why we have section 300.5(I). There is no need for is as the issue is covered in 300.3.

The wording in 300.3(B)(3) would permit any combination of phases in a non-ferrous raceway.
 
The question is a good one as the term "isolated phase" is not defined in the NEC. I can see it being read as one phase per raceway and not including more than one phase per raceway.

I don't even know why we have section 300.5(I). There is no need for is as the issue is covered in 300.3.

The wording in 300.3(B)(3) would permit any combination of phases in a non-ferrous raceway.




...but 300.3(B)(1) (exception) deals directly with parallel installations and states, 'raceways run underground shall be permitted to be arranged as isolated phase installations. IMO, if you install 2 phases in same conduit, that is not an isolated phase installation.

In full disclosure, this was addressed on another site where most of us are also members, I did forget however, that bob is a moderator over here and has a tactical advantage :cry::slaphead:. :)

I'd be interested in M Holts opinion on this, but do not know how/where to contact him
 
...but 300.3(B)(1) (exception) deals directly with parallel installations and states, 'raceways run underground shall be permitted to be arranged as isolated phase installations.

Exception 1 does address parallel installations but you are quoting exception 2.


This discussion is about exception 2 and exception 2 applies to both parallel and non-parallel installations.

IMO, if you install 2 phases in same conduit, that is not an isolated phase installation.

In full disclosure, this was addressed on another site where most of us are also members, I did forget however, that bob is a moderator over here and has a tactical advantage :cry::slaphead:. :)

[

No advantage at all, unless I cheat and edit your posts. I would not do that. :)
 
Code Commentary -- Isolated phase installations contain only one phase per raceway or cable. -- IMO does relate to parallel installations & non parallel circuits. If you are installing a 3 phase 4 wire circuit the code will regulate using either 1-conduit or 4- conduits. I do not find any code to back up using 2 conduits for a non prallel 3 phase 4 wire circuit. 300.3(B)(1) States " shall apply separately to each portion of the paralleled installation." IMO each phase = separately to each portion


 
I do not find any code to back up using 2 conduits for a non prallel 3 phase 4 wire circuit.
But, do you find any wording to prohibit it. Electrically speaking there is no problem with it.

Roger
 
...but 300.3(B)(1) (exception) deals directly with parallel installations and states, 'raceways run underground shall be permitted to be arranged as isolated phase installations. IMO, if you install 2 phases in same conduit, that is not an isolated phase installation. ...
I see no reason for that exception either. The subject matter is covered by 300.3(B)(3).

I can understand the issue with the term "isolated phase" and that is why I choose to use the rule in 300.3(B)(3) and not the rules that use the term "isolated phase".
 
Exception 1 does address parallel installations but you are quoting exception 2.


This discussion is about exception 2 and exception 2 applies to both parallel and non-parallel installations.



No advantage at all, unless I cheat and edit your posts. I would not do that. :)

meant to say ex 2 thanks for the correction. It is an interesting question. Bob, can you send the question to MHolt for opinion?
 
I see no reason for that exception either. The subject matter is covered by 300.3(B)(3).

I can understand the issue with the term "isolated phase" and that is why I choose to use the rule in 300.3(B)(3) and not the rules that use the term "isolated phase".

thats just it don, they want the phases isolated
 
thats just it don, they want the phases isolated

You are saying that like you have spoken to the people who wrote the section and you have not. You are simple telling us how you see it. :)

But how you see it makes no sense electrically. There is no safety reason to prohibit having A&B in one conduit and C&N in another conduit. (Assuming you follow all the rules in the exception.)

If we were direct burying those same conductors we could drop them in the trench in any order we want and becuse the PVC conduit is invisible to the magnetic fields the addition of PVC conduits would not change any electrcal characteristics.
 
IMO each phase = separately to each portion --- seems to prohibit it
Just because there is wording permitting one way does not automatically prohibit an alternate way.

Roger
 
IMO each phase = separately to each portion --- seems to prohibit it
That is why I use 300.3(B)(3)....there is no restricitions on it application, and in my opinion it modifies 300.3(B)(1). It remains my opinion that there is no reason for 300.3(B)(1). (B)(3) would permit what (B)(1) does and would clearly permit the installation with two phases on one conduit and the third phase and the grounded conductor in the second conduit.
 
Just because there is wording permitting one way does not automatically prohibit an alternate way.

Roger
The use of 300.3(B)(1) has to be based on the definition of "isolated phase". That is not a code defined term. I can easily see the AHJ as requiring only one phase in a raceway when that rule is used. I don't know if that is the intent or not. Again, I just bypass that rule and go to 300.3(B)(3).
 
One phase per conduit.

Isolated Phase really does not need a definition, common language term.

Isolated= separate from others, having no contact, individual
 
One phase per conduit.

Isolated Phase really does not need a definition, common language term.

Isolated= separate from others, having no contact, individual

Well we disagree, if A is in a different pipe from B they are isolated, there is nothing in the section that requires all to be isolated or any electrical reason to require all to be isolated.
 