la2151
Member
- Location
- california
I am really looking for others input? Does NEC prohibit a quad plug under the sink If both plugs are on a seperate circuit?
thanks.
thanks.
la2151 said:I am really looking for others input? Does NEC prohibit a quad plug under the sink If both plugs are on a seperate circuit?
thanks.
kbsparky said:I don't think so, but why would you want to install a quad, when you can split-wire a standard duplex?![]()
la2151 said:I am really looking for others input? Does NEC prohibit a quad plug under the sink If both plugs are on a separate circuit?
thanks.
Some cord-connected units are suitable for field conversion to permanently connected installation; conversion instructions are provided with the conversion parts kit .
Some permanently connected type dishwashers may be converted to cord connection by means of a cord kit that is available from the manufacturer of the dishwasher.
M. D. said:Some guys are getting tagged for putting them on just any old cord and plug.
hillbilly said:I've heard this.
Other than it being a requirement of the manufacturer that a particular cord must be used, I believe that as long the requirements of Article 400 are met, it's perfectly OK to make a flexible cord for a dishwasher.
I know that others will disagree, and this is only my opinion.
25.2.5 The power-supply cord shall be attached permanently to the
appliance or shall be in the form of a separate cord supplied as part of a
power-supply cord kit with means for connection to the appliance. The
power-supply cord kit shall comply with Clause 25.2A.
25.2.6 The ampacity of the cord and the current rating of the fittings shall not be less than the current
rating of the appliance.
For an appliance rated more than 15 A, the current rating of the attachment plug shall not be less than
125% of the current rating of the appliance.
A 20 A plug shall be acceptable for an appliance rated not more than 4000 W at 240 V. The attachment
plug shall be acceptable for use at a voltage equal to the rated voltage of the appliance.
.
25.2A Power-supply cord kits for use with undercounter or built-in
dishwashers
25.2A.1 A power-supply cord kit intended for the installation of an
undercounter or built-in dishwasher shall include the following:
a) power-supp ly cord, strain-relief means, and push-back relief that complies
with Clause 25.2;
b) a part or model number marked on the power-supply cord kit package, or
in the kit installation instructions;
c) installation instructions; and
d) grounding instructions in accordance with Clause 7.2.2.4(a).
480sparky said:I always run 12/3 from the disposal switch to the disposal recept and install a split recep. I also run a 12/2 to the bottom plate behind the DW and direct wire it.
Then I have a switched recep for the disposal, and a hot one for the hot water dispenser they never told me about.![]()
Energize said:I know this is not in reference to the OP, but I am wondering - why you are using 12/3 and 12/2 instead of 14/3 and 14/2 ?
Energize said:I know this is not in reference to the OP, but I am wondering - why you are using 12/3 and 12/2 instead of 14/3 and 14/2 ?
electricmanscott said:Whaaattt!!! You can't use 14 in a kitchen.:grin:
#12 is better!!!![]()
There are many who think this is true. For me, #12 only where required or needed. Dishwasher and disposal are not one of those situations.
monkey said:Are you talking two circuits? What if they get one of those 7 amp disposals and an 11 amp dishwasher?
monkey said:.... What if they get one of those 7 amp disposals and an 11 amp dishwasher?
jerm said:Maybe he's in Tulsa!
Local Rule:
SECTION 302. BRANCH CIRCUITS
302.1 Conductors. Branch circuit conductors shall not be smaller than twelve (12) American Wire Gauge (12 AWG).
(http://www.cityoftulsa.org/ourcity/ordinances/Title52.asp)
kbsparky said:Simply feed a split-wired outlet from a 3-way switch. Top half is on when the switch is up (disposal) and bottom half is on when the switch is "down" (DW).
Non-coincident loads this way ...![]()
kbsparky said:Simply feed a split-wired outlet from a 3-way switch. Top half is on when the switch is up (disposal) and bottom half is on when the switch is "down" (DW).
Non-coincident loads this way ...![]()
kbsparky said:Simply feed a split-wired outlet from a 3-way switch. Top half is on when the switch is up (disposal) and bottom half is on when the switch is "down" (DW).
Non-coincident loads this way ...![]()