Hi Everyone. Say I am having a problem with the inspectors. I wired a Dishwasher and a Disposal on the same 20A ckt. The inspector says that I need seperate ckts to each of these. The dishwasher has a FLA of 9.6A with 2.7 of that being the motor The disposal has a FLA of 6.7 all of which is the motor. According to my calculation the total Current of these two is 17.975 A Any one tell me why I can't put these on the same Ckt. The Inspector sites article 210.23 (a) (2). However there are no other loads on this ckt.