Hmmmm... Lets look at this one. Not sure of your code cycle, but I don't know if it has changed much....
[quote='02 NEC]210.23 Permissible Loads.
In no case shall the load exceed the branch-circuit ampere rating. An individual branch circuit shall be permitted to supply any load for which it is rated. A branch circuit supplying two or more outlets or receptacles shall supply only the loads specified according to its size as specified in 210.23(A) through (D) and as summarized in 210.24 and Table 210.24.
[quote='02 NEC hanbook commentary]The requirements of 210.23 are often misunderstood. An individual (single-outlet) branch circuit can supply any load within its rating. On the other side, the load, of course, cannot be greater than the branch-circuit rating. [/quote]
(A) 15- and 20-Ampere Branch Circuits. A 15- or 20-ampere branch circuit shall be permitted to supply lighting units or other utilization equipment, or a combination of both, and shall comply with 210.23(A)(1) and (A)(2).
Exception: The small appliance branch circuits, laundry branch circuits, and bathroom branch circuits required in a dwelling unit(s) by 210.11(C)(1), (2), and (3) shall supply only the receptacle outlets specified in that section.
[quote='02 NEC hanbook commentary]Section 210.23(A) permits a 15- or 20-ampere branch circuit for lighting to also supply utilization equipment fastened in place, such as an air conditioner.
The equipment load must not exceed 50 percent of the branch-circuit ampere rating (7.5 amperes on a 15-ampere circuit and
10 amperes on a 20-ampere circuit). However, according to 210.52(B), such fastened-in-place equipment is not permitted on the small-appliance branch circuits required in the kitchen, dining room, and so on. [/quote]
(1) Cord-and-Plug-Connected Equipment. The rating of any one cord-and-plug-connected utilization equipment shall not exceed 80 percent of the branch-circuit ampere rating.
(2) Utilization Equipment Fastened in Place.
The total rating of utilization equipment fastened in place, other than luminaires (lighting fixtures),
shall not exceed 50 percent of the branch-circuit ampere rating where lighting units, cord-and-plug-connected utilization equipment not fastened in place, or both, are also supplied.[/quote]
I think he is
assuming that one or the other is over 10A?
However he may be confusing this with 210.21(B)2 and would be essentially the same as applying 210.23(A)1 - as you would only if cord connected? Which it would be very easy to exceed with most GD's and DW's and pretty common these days IMO.
Like this combination: Both are over 50%, and combined over 80% (if cord connected), and total ~110% of the circuit rating.
10.2A
12A
But if you can have a "badger" GD - and an older no bells and whistles DW installed at final.... You might be hard pressed to find a new dishwasher that is either less than 12A, or that does other than state 15A* as a circuit requirement. (* failing to state the actual - but you would have to go off of nameplate once it got there, and would likely be over 10A.)