Dishwasher Breaker Size

Status
Not open for further replies.

Electricalhelp

Senior Member
Location
NJ
If I have a dishwasher that is 480V, 3 Phase and it drawings 27 AMPS.

What will be the breaker size, should I go with 27*1.25 = 33.75 Amps.

Should I go with 30 or 40 AMP breaker.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Showing a chart from online means nothing. You need the nameplate rating of the equipment. What size wire are you running? Does the equipment actually draw 27 amps.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If I have a dishwasher that is 480V, 3 Phase and it drawings 27 AMPS.

What will be the breaker size, should I go with 27*1.25 = 33.75 Amps.

Should I go with 30 or 40 AMP breaker.

Why add the 25%? The load is 27 amps non-continuous so 30 amp circuit.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Don't motors and heaters need to be at 125%

A dishwasher is an appliance so you can use the nameplate to size the branch circuit. Also it's not a continuous load so the 27 amps is what you would use to find the minimum branch circuit size.
 