GerryB

Senior Member
I'm sure this has come up before, but why is there an exception for the refridgerator in 210.52.B and not the dishwasher? Let's you have two 20 amp counter topcircuits, have an individual 15 amp circuit for the fridge, can you run another individual 15 amp ckt for the dw?
 

Lanesmith

Member
Location
Texas
Yes you can run separate for dishwasher I always have. And you can have more than two appliance ckts. You can only have 2 devices or outlets per appliance ckt.

Sent from my SAMSUNG-SM-T337A using Tapatalk
 

kwired

Electron manager
Location
NE Nebraska
Dishwasher is not permitted to be on a SABC.

Refrigeration equipment is included in the SABC's. The 15 amp circuit exception is for refrigerators only - but is still part of the SABC's

You can run two SABC's to a kitchen as well as run outlets in the dining room, pantry, breakfast room, or other similar rooms off those same two circuits - and have no other SABC's in the house. A second kitchen will require at least two more SABC's though.

A small enough kitchen may just have two outlets on the SABC's. A large kitchen could have 100 outlets on SABC's and still only two circuits, might not be good design but does pass NEC.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
I'm sure this has come up before, but why is there an exception for the refridgerator in 210.52.B and not the dishwasher? Let's you have two 20 amp counter topcircuits, have an individual 15 amp circuit for the fridge, can you run another individual 15 amp ckt for the dw?

You can run a circuit for the DW but it has to be a 20A, not 15A as the exception is only for refrigerator.

Yes you can run separate for dishwasher I always have. And you can have more than two appliance ckts. You can only have 2 devices or outlets per appliance ckt.

Sent from my SAMSUNG-SM-T337A using Tapatalk

I don't see where you are coming up with "only two devices or outlets per appliance ckt".
 

kwired

Electron manager
Location
NE Nebraska
You can run a circuit for the DW but it has to be a 20A, not 15A as the exception is only for refrigerator.



I don't see where you are coming up with "only two devices or outlets per appliance ckt".

DW is not on the list of things that must be on SABC's, it is excluded from SABC's by "shall serve no other outlets" (or something very close to that anyway) it does not need to be a 20 amp unless the capacity of the appliance dictates that.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
DW is not on the list of things that must be on SABC's, it is excluded from SABC's by "shall serve no other outlets" (or something very close to that anyway) it does not need to be a 20 amp unless the capacity of the appliance dictates that.

Agreed

Chris
 

FionaZuppa

Senior Member
Location
AZ
Occupation
Part Time Electrician (semi retired, old) - EE retired.
You can run a circuit for the DW but it has to be a 20A, not 15A as the exception is only for refrigerator.
if its dedicated ckt (one recept or hardwired), why 20A ? not an NEC Q, just a general Q.
 

jumper

Senior Member
I'm sure this has come up before, but why is there an exception for the refridgerator in 210.52.B and not the dishwasher? Let's you have two 20 amp counter topcircuits, have an individual 15 amp circuit for the fridge, can you run another individual 15 amp ckt for the dw?

Note that in the 2017 NEC any appliance, not just refrigeration units, can be on a dedicated/individual circuit even if that that space is in the SABC area.
 

peter d

Senior Member
Location
New England
I'm sure this has come up before, but why is there an exception for the refridgerator in 210.52.B and not the dishwasher? Let's you have two 20 amp counter topcircuits, have an individual 15 amp circuit for the fridge, can you run another individual 15 amp ckt for the dw?

Yes, in my area it's standard practice to run a dedicated 15 amp circuit for the DW and has been for a long time. I've never heard of or had an issue with this and have never encountered a need for a 20 amp circuit for the DW.
 

kwired

Electron manager
Location
NE Nebraska
Note that in the 2017 NEC any appliance, not just refrigeration units, can be on a dedicated/individual circuit even if that that space is in the SABC area.
Unless there was a change in 2017, you could do that before as well.

If you ran a single receptacle outlet to a counter top receptacle, you might have "microwave outlet" in mind, but many will still see that as an additional SABC and an additional 1500VA for load calculations as well.

If you ran the same single receptacle branch circuit to same spot but they built a cabinet around it to house the microwave - you might be able to call it a dedicated circuit and not a SABC, and might even be able to make it a 15 amp circuit if you wanted. You would't have a 1500 VA load for that receptacle but have whatever the appliance rating is in your load calculations (if you can get away from it being considered a SABC, I think many AHJ's will still call that one a SABC outlet if it is below 5',6"(?) from the floor)
 