electrabishi
Member
- Location
- Alaska
- Occupation
- EE
In going through the 2023 Code Review course this year there is an Authors comment in section 23 Changes - Article 422 – Appliances, that states "The receptacle for the dishwasher is not permitted to be a GFCI because it is not in a readily accessible spot as required by 210.8"
However 210.8(A)7 requires receptacles within 6 ft of the sink to be GFCI protected.
Why would under a sink not be accessible by opening the door, much as opening the drawer under a range allows the range outlet to be considered accessible?
However 210.8(A)7 requires receptacles within 6 ft of the sink to be GFCI protected.
Why would under a sink not be accessible by opening the door, much as opening the drawer under a range allows the range outlet to be considered accessible?