Sprint
Member
- Location
- Albany, N.Y.
- Occupation
- Technician
I have a customer that would like me to install a commercial dish washer
However, he would like to make it portable
I sized the conductors at #10 awg
I was going to use 15ft of SO Cord
With the appropriate NEMA twist locks
Since it will be next to the SS sink I would like to put it on a 30 amp GFCI
However, there is no neutral on the Dishwasher
So the neutral on the breaker would be considered open
How can I protect the circuit or do I need to?
Thanks
However, he would like to make it portable
I sized the conductors at #10 awg
I was going to use 15ft of SO Cord
With the appropriate NEMA twist locks
Since it will be next to the SS sink I would like to put it on a 30 amp GFCI
However, there is no neutral on the Dishwasher
So the neutral on the breaker would be considered open
How can I protect the circuit or do I need to?
Thanks