revosolution

New member
can someone help figure out if you need to have a switch disconnect for the dishwasher other than the one on the machine for chicago code? thanks
 
revosolution said:
can someone help figure out if you need to have a switch disconnect for the dishwasher other than the one on the machine for chicago code? thanks


I dont know about Chicago code, but the nec requires a disconnect if the unit switch does NOT break the ungrounded conductors.

Start at 422.30
 
I'm curious where 422.32 comes in. I would have thought the dishwasher is motor driven and over 1/3 hp. Which if I understand correctly the disconnect would have to be within sight.
 
SmithBuilt said:
I'm curious where 422.32 comes in. I would have thought the dishwasher is motor driven and over 1/3 hp. Which if I understand correctly the disconnect would have to be within sight.

Apparently there are some dw with only 1/8 hp motors. Hard to believe--- I have never used a breaker lock for this reason-- It is easy enough to add a switch.
 
Jim W in Tampa said:
Breaker lockout is all thats required.They must be the type that stays on the breaker and is ready for small pad lock.Its fastest and cheapist way.


I doubt it Jim, unless the dishwasher is under 1/8th horse power... very unlikely.
 
Jim W in Tampa said:
Its all i did on hundreds and passes.

Lots of jobs get passed even when things are not code compliant. Perhaps you had 1/8 hp motors but chances are the inspections is not catching it. I bet if I did not install a breaker lockout nor a disco in sight for my dw's they would still pass in most of my jurisdictions. That doesn't make it code compliant
 
just out of curiosity (we don't wire houses, it's been something like 15 years since I had anything to do with wiring a house) where would you put the disconnecting switch? in the cavity behind the dw?
 
jerm said:
just out of curiosity (we don't wire houses, it's been something like 15 years since I had anything to do with wiring a house) where would you put the disconnecting switch? in the cavity behind the dw?

ANywhere that is in sight of the motor controller
 
jerm said:
just out of curiosity (we don't wire houses, it's been something like 15 years since I had anything to do with wiring a house) where would you put the disconnecting switch? in the cavity behind the dw?


Ever wire a commercial dishwasher? the same rules apply.
 
jerm said:
just out of curiosity (we don't wire houses, it's been something like 15 years since I had anything to do with wiring a house) where would you put the disconnecting switch? in the cavity behind the dw?

I put it in the cabinet under the sink. The standard procedure around here has always been to float a switch box under the dw with a sp switch and handy box sw. cover.

I know it's not legal but that was the accepted practice. Now with all the dw that have no space under them I just install a switch in the sink cabinet. I leave a tail out for the dw and if the dw comes with a cord & plug I disconnect the tail and just put a receptacle in the box under the sink.
 
stickboy1375 said:
Ever wire a commercial dishwasher? the same rules apply.
Yeah, but we mount a wet location disconnect (nema 4 or 12?) on the FRP with FMC or FNMC out the bottom into the (generally 3o) washer... These clean up rooms get hosed down top to bottom every so often.

Never wired one inside a cabinet space besides my own here at the house, and it doesn't have any disconnect within sight btw... I guess the two wirenuts don't count. ;)

2008 NEC 225.22 EXCEPTION DELETED
Fexible metal conduit is no longer permitted to be used in wet locations.
egad. our dishwasher installs have all been considered "wet locations." I guess FNMC is still okay?
 
Last edited:
SmithBuilt said:
I'm curious where 422.32 comes in. I would have thought the dishwasher is motor driven and over 1/3 hp. Which if I understand correctly the disconnect would have to be within sight.

I'm wondering where 422.31(B) would apply to an HP-rated appliance in that case. I guess I'm wondering what type of appliance might be "rated over 1/8 hp" (422.31(B)) and not be a "motor driven appliance of more than 1/8 hp" (422.32).

Perhaps I'm confused by the wording. I can see that a dishwasher with a pump motor < 1/8 hp would fall into 422.31(B) (because the heater would take it over 300VA) but not 422.32.

Dave
 