I am confused. 450.3(B) states that if I size my primary breaker at <125% of the transformer rating, that primary protection is adequate.
240.4F says that with a standard delta-wye transformer, I do need protection of the secondary conductors. The application here is a 30 or 45kva transformer in a room fed from a 480V distribution board. The transformer sits on the floor and a 120/208 volt panelboard is on the wall next to it. What is the correct way to install the transformer/panelboard combo. Does the panelboard need a main breaker? If it has a main bkr, does that meet 240.4F. Or does it need a separate secondary disconnect switch? The 480 volt source could be in the same room or not in the same room.
240.4F says that with a standard delta-wye transformer, I do need protection of the secondary conductors. The application here is a 30 or 45kva transformer in a room fed from a 480V distribution board. The transformer sits on the floor and a 120/208 volt panelboard is on the wall next to it. What is the correct way to install the transformer/panelboard combo. Does the panelboard need a main breaker? If it has a main bkr, does that meet 240.4F. Or does it need a separate secondary disconnect switch? The 480 volt source could be in the same room or not in the same room.