In a word, yes!We have a 4/0 bare grounding conductor going around a module ouside of it, the contractor used unistrut straps (B-Line B1508S) to attach it to unistrut. Is there a problem with dissimilar metals corroding, it is by the ocean (Prudhoe Bay, AK)?
In a word, yes!
Look to use insulating plastic bushings or similar measures to keep the two metals from direct contact.
What could or would happen to the ground wire?
Bare copper conductors are installed inside steel raceways everyday.
I am not so sure it is an issue to worry about.
Where can we find a formula/table for calculating this corrosion factor?Contact over a very wide area (as inside a steel raceway) is not going to pose the same level of corrosion problem as a few small point contacts.
Current density determines the degree to which a particular small part of the wire will be corroded.
Also, FWIW, inside a steel raceway will not be as bad as with direct salt spray exposure.
The true test will be in watching the support area over the first year. Then it will be time to make a decision on whether to do anything. A thick enough wire will last a lot longer.![]()
Which opens the door to another question........What is it that is so great about copper ground rods?Forgot to mention that solid will last a lot longer than stranded.
Although 4/0 solid would be a lot more like a rod electrode than a GEC.
Also, FWIW, inside a steel raceway will not be as bad as with direct salt spray exposure.
Not much. In fact, they can cause failure of nearby steel structures by corroding them, if soil resistivity is good.What is it that is so great about copper ground rods?
We have a 4/0 bare grounding conductor going around a module ouside of it, the contractor used unistrut straps (B-Line B1508S) to attach it to unistrut. Is there a problem with dissimilar metals corroding, it is by the ocean (Prudhoe Bay, AK)?
Nothing will happen in terms of dissimilar metals. Stainless steel doesn't react with anything...... i really don't know if it's the galvanized unistrut or the stainless steel tubing that will give way first.
FIFYNothing will happen in terms of dissimilar metals. Stainless steel doesn't react very much with anything.
I think you used that word on me once before. I had to look it up again.electronegativity
I think you used that word on me once before. I had to look it up again.
We have a 4/0 bare grounding conductor going around a module ouside of it, the contractor used unistrut straps (B-Line B1508S) to attach it to unistrut. Is there a problem with dissimilar metals corroding, it is by the ocean (Prudhoe Bay, AK)?