Dissimilar voltages in the same raceway

Status
Not open for further replies.

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Dissimilar voltages in the same raceway

If you do this please don't forget about the identification rules in 210.4(D).
Don
 

ryan_618

Senior Member
Re: Dissimilar voltages in the same raceway

Don I agree with your post, but what if they were not multi-wire branch circuits? I think identification of voltage system should not be required only on a multi-wire circuit. Just my two cents.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: Dissimilar voltages in the same raceway

Ryan, there is a proposal for the 05 NEC for just what you stated.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Dissimilar voltages in the same raceway

And contrary to popular opinion, you can't use white for the grounded conductor of one system and gray for the second system when the conductors are in a common raceway or enclosure.
Don