Dissipative heat of transformers

Status
Not open for further replies.

m sleem

Top-notch Сasual Dating - Real-life Females
Location
Usa
Occupation
Health
Which one we should consider for the dissipative heat of transformers:

- load loss.
- no-load loss.
- both.
 
Not sure I understand your point.
The most heat dissipated by the transformer is when it is delivering its rated kVA.
From vendor catalog you can find two different values of VA (load loss & no-load loss). for HVAC engineers which value they should consider as a heat dissipation.
 
From vendor catalog you can find two different values of VA (load loss & no-load loss). for HVAC engineers which value they should consider as a heat dissipation.
I've never seen it put that way.
But maybe a reasonable assumption is that no load loss is primarily Fe loss and on load loss is primarily the Cu loss.
On that basis I would sum them.
 
I have the same for dry-type. Please check View attachment 7658
View attachment 7659

If load loss includes no-load loss hence we should consider load loss only.

Looking at the ABB data the second time, you should confirm it with ABB if the "load loss" includes the no load losses. I am more used to see "full load loss" or "nameplate rating load loss". At motors, the FLA includes the No Load Amperes.
 
Load or winding loss is defined to be the losses that occur under load but do not exist at no-load. They are almost entirely resistance related and are also called copper loss.

The no-load losses are the iron losses, dielectric losses, and the copper loss due to exciting current. Also called iron loss.

The total losses are the sum of the load and no-load losses.
 