Worst case loss, if that's what you want, is loaded at rated load.Which one we should consider for the dissipative heat of transformers:
- load loss.
- no-load loss.
- both.
Worst case loss, if that's what you want, is loaded at rated load.
Not sure I understand your point.Means that at (load loss).
From vendor catalog you can find two different values of VA (load loss & no-load loss). for HVAC engineers which value they should consider as a heat dissipation.Not sure I understand your point.
The most heat dissipated by the transformer is when it is delivering its rated kVA.
I've never seen it put that way.From vendor catalog you can find two different values of VA (load loss & no-load loss). for HVAC engineers which value they should consider as a heat dissipation.
I've never seen it put that way.
But maybe a reasonable assumption is that no load loss is primarily Fe loss and on load loss is primarily the Cu loss.
On that basis I would sum them.
Please take a look to the attachedView attachment 7653.
I have the same for dry-type. Please check View attachment ABB Catalog-Page 30.pdfFull load loss already includes the no-load loss. If you do not expect your transformer fully loaded, you can extrapolate between those two numbers. It is unlikely though that the attached oil filled transformer would be installed indoors, needing HVAC.:lol:
I have the same for dry-type. Please check View attachment 7658
View attachment 7659
If load loss includes no-load loss hence we should consider load loss only.
Both.Which one we should consider for the dissipative heat of transformers:
- load loss.
- no-load loss.
- both.