distance between boxes

Status
Not open for further replies.

jimmy3214

Member
Location
Indiana
I have been in the trade for 13 years now.. ever since i started I have been told that there has to be no more than 100 feet between boxes on a conduit run. Where does it state this in th code book?
 

hornetd

Senior Member
Location
Maryland
Occupation
Journeyman Electrician, Retired
Re: distance between boxes

Think about duct banks and well circuits. Hundreds of feet of continuous raceway is perfectly normal.
--
Tom
 

Len_B

Member
Location
New Hampshire
Re: distance between boxes

We would sometimes put C's in every 90'-100' for (fish tape) convenience but code only requires access at every 360 deg for pulling. I've blown mice well over 1000'.

edit: oops! (This was over ten years ago) Total run was approx 1500', there was an underground pull box at about 800', still a long run though.

[ March 03, 2003, 06:51 PM: Message edited by: Len_B ]
 