M mortimer third party inspector Location New England Occupation retired Feb 5, 2019 #1 code section please:ashamed1:
N nickelec Senior Member Location US Feb 5, 2019 #2 Not an nec code I'm pretty sure the nec does not even mention smokes Sent from my SM-G965U using Tapatalk
kwired Electron manager Location NE Nebraska Occupation EC Feb 5, 2019 #3 I can tell you it is not anything in NEC.
Vince1971 Member Location Eden, NC Feb 5, 2019 #4 min. 3' from blade edge. Manufacturers Installation Instructions. See also NFPA 72.
M mortimer third party inspector Location New England Occupation retired Feb 5, 2019 #5 :thumbsup::thumbsup:
JohnE Senior Member Location Milford, MA Occupation Electrical Contractor, Inspector Feb 5, 2019 #6 Vince1971 said: min. 3' from blade edge. Manufacturers Installation Instructions. See also NFPA 72. Click to expand... Yes, this requirement is in NFPA 72. Similarly, smokes need to be 3' from HVAC register.