Distance between Manholes - Is there a NEC Requirement
Our Estimator is planning to offer a credit for an Underground installation that includes UG conduit & manholes, per plans/drawings. His plan is to bore approximately 1200' and pull the 12-kv conductors - through the bored conduit(s) from the first/ beginning manhole to the end/last manhole. The 1200' would be a straight pull. Our boss thinks there is a maximum distance allowed for the Underground conduit and a manhole or manholes must be installed, per the NEC. Oh yes, we are in the 2017 NEC cycle, in case that makes a difference. I haven't found anything in the 2017 NEC that would place a distance between manholes for an UG conduit installation. I did ask our Estimator to check with the cable manufacturer to see if there was any limitations on the conductors for that type of pull.
Can anyone come up with a NEC reference limiting the 1200' pull and placing manholes in the UG conduit installation?
Thanks,
To my knowledge, there is no such requirement. Manholes have requirements when they are used, but their spacing is determined by other practical considerations (bend limits, how long of a single conductor you can get, etc...) rather than any specific length.
I reckon the maximum would be (roughly) around 25,000 miles / 40,000 kilometers, the circumference of the earth. Any more and you'd be over the 360° of bends allowed.
And you are also limited by the max pulling tension of the cable, check with mfg and there is software available to calculate
You will exceed the factory length of your cable, before the Earth's curvature contributes even a hundredth of a degree. The curvature in local terrain is going to impact the bend accumulation a lot more than the global curvature.
Splicing has to occur in an access point, so the spool length will be the important limit on pull point spacing.
  • Like
Reactions: jap