You mentioned this was for area lighting at a reservoir site.
It's fairly standard/typical, that the electrical specs for water utility/public works projects, require UGPBs for branch circuits and control wiring to be strategically placed in 200' intervals ("strategically placed" refers to physical area of placement over exact lineal distance, e.g. keep away from lower ground like drain swells/grates, heavy vehicle traffic areas, non-practical access areas, etc. future accessibility/convenance should be considered as well as stub-up placement/arrangement in box, size of box, proper ID of all conduit & wire, and any future known needs that can be achieved through this box, should be addressed at this time, even if its just one EL/stub and a couple feet of pipe, extending beyond the "you may as well dig-up the box now" point, and preferably heading where it can do the most good).
Duct seal all the stubs before closing the lid for the last time, which will require removing all of the temporary protection of each stub, like duct tape, rags, anything you used to ensure clean conduit systems.