Distance from window

Status
Not open for further replies.

ddaut

Member
Location
Louisiana
Occupation
Electrician
I understand that the weaterhead and drip loop need to be 3' away from the window but what about the service riser and meter can? Can I mount the meter can and service riser less than 3' along the side of the window and use the riser to go high above the window near the roof? This will be for a side of the house attachment.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
The riser and meter can do not have to be any particular distance from a window.
 

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
In California this is what Southern California Edison requires.
 