i also work in a place with several 480vac 3 ph equipment. you may want to look at CFR 1910.3xx for general industry. The clearance rules may depend on the date of the installation. can be 24".
edit to add: not 24 but 30"
1910.303(g)(1)(vi)(B)
For installations built on or after August 13, 2007, 1.98 m (6.5 ft), except that where the electrical equipment exceeds 1.98 m (6.5 ft) in height, the minimum headroom may not be less than the height of the equipment.
Table S-1. -- Minimum Depth of Clear Working Space at
Electric Equipment, 600 V or Less
Nominal voltage to ground Minimum clear distance for condition2 3
Condition A Condition B Condition C
m ft m ft m ft
0-150
151-600 10.9
10.9 13.0
13.0 10.9
1.0 13.0
3.5 0.9
1.2 3.0
4.0
Notes to Table S-1:
1. Minimum clear distances may be 0.7 m (2.5 ft) for installations built before April 16, 1981.
2. Conditions A, B, and C are as follows:
Condition A -- Exposed live parts on one side and no live or grounded parts on the other side of the working space, or exposed live parts on both sides effectively guarded by suitable wood or other insulating material. Insulated wire or insulated busbars operating at not over 300 volts are not considered live parts.
Condition B -- Exposed live parts on one side and grounded parts on the other side.
Condition C -- Exposed live parts on both sides of the work space (not guarded as provided in Condition A) with the operator between.
3. Working space is not required in back of assemblies such as dead-front switchboards or motor control centers where there are no renewable or adjustable parts (such as fuses or switches) on the back and where all connections are accessible from locations other than the back. Where rear access is required to work on deenergized parts on the back of enclosed equipment, a minimum working space of 762 mm (30 in.) horizontally shall be provided.