Distance of Arcfault Rec. from panel

Status
Not open for further replies.
The length requirements only come into play when you are applying 210.12(A)(3) or (4).

210.12(A)(3) requires the circuit originate at a "listed supplemental arc protection circuit breaker". That breaker does not exist and probably never will as there is no standard to build such a breaker.

210.12(A)(4) requires that the circuit originate at an AFCI of the branch circuit/feeder type. That is the type of the original AFCI breakers and would likely cost just as much as the currently required combination type AFCI breaker.
 