What is to be considered the distribution point in this sentence as stated in 700.9(B)
Wiring from an emergency source or emergency source distribution overcurrent protection to emergency loads shall be kept entirely independent of all other wiring and equipment
Is this the breaker on the emergency generator, or the disconnect as the feeder enters the building? The switch board? What if we have 700, 701, and 702 in the same panleboard, is this independent?
Wiring from an emergency source or emergency source distribution overcurrent protection to emergency loads shall be kept entirely independent of all other wiring and equipment
Is this the breaker on the emergency generator, or the disconnect as the feeder enters the building? The switch board? What if we have 700, 701, and 702 in the same panleboard, is this independent?