Hi
I have an existing 600A service with fuse main and with no distribusion section
is it practical to install a new properly sized gutter adjacent
and extend the 600A conductors into it
then, tab three times from this 600A with 3/0 cu to three sub panels with main ocpd ( again , allinstalled adjacent) ?????

Thank you
 

kwired

Electron manager
Location
NE Nebraska
Hi
I have an existing 600A service with fuse main and with no distribusion section
is it practical to install a new properly sized gutter adjacent
and extend the 600A conductors into it
then, tab three times from this 600A with 3/0 cu to three sub panels with main ocpd ( again , allinstalled adjacent) ?????

Thank you
If the conductors are 600 amp there is no limit on how far they can extend. The taps are what have limitations, unless outdoors.

There also is no limitation to the number of taps you can make. At some point though the amount of load will reach your 600 amp fuse limitation though.
 