Distribution Service -Code compliance

Status
Not open for further replies.

zazmat

Member
I have a project where I am trying to install equipment for distribution service to two different buildings in a substation facility.

The distribution service from a normal and alternate source will be fed via ATS (located on the inner wall of first kysor building- Control Center#2) to two 225A panels via 225A breakers. The service cable from ATS will also be fed to the second building (Control Center #1)150A breaker via a 225A breaker located isnde CC#2.

Please refer to the attached drawing. (service side of ATS not shown)

My question for you all is, do you see any code violation?

Does it comply with NEC 230.3? If not, what is the reasoning behind complying with NEC 230.3?

Also, most importantly are you aware of any breaker panel, which would carry all three 225A breakers within one assembly (items inside dashed line) and has a small form factor to be mounted inside control center 2?

I will appreciate your advice.
 

zazmat

Member
If you notice carfeully there are three breakers inside the dashed line. each breaker is feeding a panel.

One is feeding AC Panel 1 in CC#2
One is feeding AC Panel 2 in CC#2
One is feeding 150A breaker in CC#1 then a panel (not shown).
 