designer82
Senior Member
- Location
- Boston
We have a large Electrical Room that will house 12 MCC'S rated 480V-3PH
There will be a Switchgear Substation just outside not far from this Electrical Room.
The design problem we're having is that running all the feeders in underground ductbanks from the Switchgear Substation to the Electrical Room is prohibitive ampacity wise (calculated in ETAP - significant derating requires 7 sets 750kcmil to each MCC... too much)
Running many cable trays is possible but it's MANY cable trays. 1 for each MCC would be 12 total 30" wide cable trays.
What about running 1 or 2 large cable trays or cable busses with enough power to feed all 12 MCC'S then using a large transition box inside the Electrical Room to tap from to each individual MCC from there? Is this practical?
What is your experience with a situation like this and the typical design approach?
Thanks
There will be a Switchgear Substation just outside not far from this Electrical Room.
The design problem we're having is that running all the feeders in underground ductbanks from the Switchgear Substation to the Electrical Room is prohibitive ampacity wise (calculated in ETAP - significant derating requires 7 sets 750kcmil to each MCC... too much)
Running many cable trays is possible but it's MANY cable trays. 1 for each MCC would be 12 total 30" wide cable trays.
What about running 1 or 2 large cable trays or cable busses with enough power to feed all 12 MCC'S then using a large transition box inside the Electrical Room to tap from to each individual MCC from there? Is this practical?
What is your experience with a situation like this and the typical design approach?
Thanks