I am to design for my company a distribution panel that will supply power to the following quipment:
Air compressor 4 nos each having a starting current of 175A on a ( star/deltal starter) and a running current of 85A each.
1 nos vacum generator with a starting current of about 52A(DOL Starter)and a runing current of 18A and another vaccum generator with a starting current of 50A and a running current of 13A.
The 2 vaccunm generator are to be swithed on first while each of the compressors are to be switched on one after the other, 3 0f the compressors will works at a time while the 4th compressor is used as a spare.
I came up with the following design:
200A 4nos circuit breaker for each of the air compressors while I provided 100A each for the vaccum generator. I also provided for spare breakers one each of 200A and 100A.
For the "main" breaker to be used for the distribution panel I am thinking of using a 600A MAIN CIRCUIT BREAKER OR A 400A CIRCUIT BREAKER
The 400A main circuit breaker seems to be adequate but considering the starting currents for the compressor I would want to favour the use of the 600A circuit breaker.
the total steady state current for all the loads are (85+85+85+13+18)=286A.
Your advice on the best option for this design will be greately appreciated.
please not the equipments are to be run on a 3 phase 400v power supply.
Air compressor 4 nos each having a starting current of 175A on a ( star/deltal starter) and a running current of 85A each.
1 nos vacum generator with a starting current of about 52A(DOL Starter)and a runing current of 18A and another vaccum generator with a starting current of 50A and a running current of 13A.
The 2 vaccunm generator are to be swithed on first while each of the compressors are to be switched on one after the other, 3 0f the compressors will works at a time while the 4th compressor is used as a spare.
I came up with the following design:
200A 4nos circuit breaker for each of the air compressors while I provided 100A each for the vaccum generator. I also provided for spare breakers one each of 200A and 100A.
For the "main" breaker to be used for the distribution panel I am thinking of using a 600A MAIN CIRCUIT BREAKER OR A 400A CIRCUIT BREAKER
The 400A main circuit breaker seems to be adequate but considering the starting currents for the compressor I would want to favour the use of the 600A circuit breaker.
the total steady state current for all the loads are (85+85+85+13+18)=286A.
Your advice on the best option for this design will be greately appreciated.
please not the equipments are to be run on a 3 phase 400v power supply.