F funseebee Member Location CA Feb 23, 2015 #1 What's normally the approximate allowed diversity factor for an existing apartment building with 42-meters?
Smart $ Esteemed Member Location Ohio Feb 23, 2015 #2 funseebee said: What's normally the approximate allowed diversity factor for an existing apartment building with 42-meters? Click to expand... 28% where 42 meters = 42 apartments and calculating load under the 200.84 optional method. Standard method is more complex in that no actual demand factoring can be given based on the number of meters/apartments.
F funseebee Member Location CA Feb 23, 2015 #3 Diversity or Demand Factor Diversity or Demand Factor Where do I find 200.84 Optional Method? Is that a section in NEC? If so, then, there's no section in NEC with 200.84. Please clarify. Thanks.
Smart $ Esteemed Member Location Ohio Feb 24, 2015 #4 funseebee said: Where do I find 200.84 Optional Method? Is that a section in NEC? If so, then, there's no section in NEC with 200.84. Please clarify. Thanks. Click to expand... It's a typo. Should have been 220.84