Q. We have a 480-277V, 3 phase, 4 wire, 2000A Service entrance main switchgear that feeds 1243 KVA mechanical loads in addition to 400 KVA
of lighting and recepticales (utlization volt for them is 120V)
The 400 KVA load has been calculated as 100% lighting load 100% equipment loads and first 10KVA of receptical loads + 50% of the remaning receptacles. To size the transformer for the above described
400 KVA load ? could we apply a 75% diversity factor to total connected loads and choose 300KVA transformer??