I am designing a new office space. Receptacle circuits will be fed with an underfloor wireway. Per Article 376 and 310.15(B)(2)(A), I have to derate for over 30 conductors. The fine print note refers to table B.310.11 in Annex B (adjustment factors for load diversity).
Question #1: Can I claim I have a 50% load diversity on these receptacle circuits?
My basis would be that it is a 45000 sq ft office; at 1VA/sq ft, I need 23 branch circuits, and I plan to provide over 100 branch circuits.
I could also use the fact I will have 6 duplexes per branch circuit. And at 180VA per duplex, thats only 720VA per 20A circuit.
Say I can claim 50% diversity and I use table B310.11. I place 42 conductors in a wireway, and use the 60% derating factor. Can I still use #12 wire with 20A breakers?
The 90 deg. ampacity of #12 is 30 Amps. 30 Amps *0.6= 18 Amps. So I can protect the wire with the next size breaker, or a 20A. Yes, or no?
Steve
Question #1: Can I claim I have a 50% load diversity on these receptacle circuits?
My basis would be that it is a 45000 sq ft office; at 1VA/sq ft, I need 23 branch circuits, and I plan to provide over 100 branch circuits.
I could also use the fact I will have 6 duplexes per branch circuit. And at 180VA per duplex, thats only 720VA per 20A circuit.
Say I can claim 50% diversity and I use table B310.11. I place 42 conductors in a wireway, and use the 60% derating factor. Can I still use #12 wire with 20A breakers?
The 90 deg. ampacity of #12 is 30 Amps. 30 Amps *0.6= 18 Amps. So I can protect the wire with the next size breaker, or a 20A. Yes, or no?
Steve