Hi everybody. First time on here. Seems every time I do a search for electrical stuff, I always find something useful from this site so figured I'd try to resolve my dilemma with you guy's help.

I'm connecting a 200 amp single phase 120/240V genset to my freshly installed ATS. The genset is on wheels and is considered semi-permanent. I'm using ~ 50Ft of 4/0 DLO cable to connect the genset to my house (with a 200A service). Electrician installed the ATS and it's all hooked up except for the genset connections.

The dilemma involves attaching the DLO cable to the transfer switch and genset terminal blocks. I know fine stranded welding cable doesn't work so well in a terminal block. The DLO cable seems to work better but still not real happy with the appearance of wire strands being pushed off to the sides when tightening the lock screw down. After a couple of days searching I can across what's called "Shoo-pin flex cable adapters".

This seems to be the perfect solution but the price is ridiculous ($48/ea) . I need at least 8 of these things. I ordered a 11-ton hyd die-type lug crimper and it should be here tomorrow. My plan was to use it to install the crazy expensive Shoo-pin adapters. However, after staring at the connectors for bit, I relaized with the crimper and some 4/0 stiff wire (THNN?) , I could make my own. I've found some "heavy duty" 4/0 tinned-copper non-insulated butt-connectors with a 0.080" wall thickness for ~$7/ea.
They're extra long so I can crimp twice on each end. Add a section of shrink wrap to pretty it up and seems like it would work just fine.

Seems like the perfect solution. Anyone see why this would not work?
Anyone got a better idea??

Thx,
John
 
This site is designed for:
  • Contractors
  • Electricians
  • Engineers
  • Inspectors
  • Instructors
  • Other electrically related individuals
This NEC® Forum is for those in the electrical and related industries. Questions of a "How-To" nature by persons not involved in the electrical industry will be removed without notice.

Knowledge and the practical application of the National Electrical Code is an essential part of all electrical installations. If it's important for you to understand the National Electrical Code, then look no further.

To better help us serve you, please be sure to update your account details with your occupation field and location if you have not done so already. You can access your account details by clicking on your account name at the top right of the page when on the forums.
 
What you are planning would not be code compliant and could be problematic. High strand count wire requires special crimps and dies. If you don’t know that or don’t have the proper tools, you probably shouldn’t be doing this.
 