I'm installing a 1200A 3Phase 4 Wire 120/208V service. I'm feeding the CT cabinet with 3 sets of 600mcm from the pad mount transformer. The problem that I'm having is getting the MDP to line up in a reasonable manner, on the other side of the wall with the CT cabinet. The bends in the wire are going to be very difficult to make. I'll have 16 600mcm conductors all twisted up in a very small area, plus the 16 conductors coming into the CT's line side! So, I've been doing some research and I came across a single conductor cable, DLO. The cable is about 2x's as much/foot, but its worth the aggravation. The ampacity rating for DLO 646.4mcm @ 75 C is 730A. So now I believe that I can go from 3 sets to 2 parallel sets. Additionally, I think I can move down to the next size, which is DLO 535.3mcm (645A @ 75 C). I don't think that I have to do any corrections for 3 or more current carrying conductors in a conduit, because, my "nipples" through the wall are only 14". I'm using the 75 C column, because, the lugs on the breaker are rated at that temperature. The cable's insulation is RHH/RWH and rated at 2000V. I'm leaning towards this, because it's made with tinned stranded wire, which will provide the flexibility that I'm going to need. I'll use uninsulated wire ferrules at my termination points. Does anybody see any issues that I might run into?