I have a job that requires installation of a 500kw inverter in Canada. I'll be running DLO/RHW-2/RW90 wire. The wire specs rate the ampacity at ambient temp. 30c. I'm looking for a wire size rated for 400amp at 75C with. Do I use DLO 373 MCM or DLO 444 MCM. The 500kw puts out 1470amp at 200v. I'll be running 4 sets in a metal wireway. NEC allows up to 30 wires before de-rating, but the nec chart 310.16 only says up to 3 wires. I'm used to running THHN and the amp rating on that but this DLO MCM rating has me confused.