MoorePowerSystems
Member
- Location
- Albany, NY
- Occupation
- Electrical/Instrumentation Contractor
I've always been told DLO/Welding cable/very fine stranded copper conductors have a higher ampacity than their courser stranded counterparts, but I cant find anything to support that. Customer wants 400amp fuses replaced with a 500 amp fuses, load side is parallel 4/0 super fine stranded conductors that go to a cable tray type cable. (I say cable tray type because its in a cable in a tray, but not tray rated, its part of a skid). According to 310.16 my 4/0 wire is only good for 230 amps. Is there anything I'm missing?