I have an NEC question that I cannot find a specific answer to:
Every panel schedule I have ever seen applies 125% to continuous loads to calculate the load for the panel. This calculation is typically used to size everything from the conductors, to OCPD, to panels and transformers.
There are clear NEC sections about applying the 125% for continuous loads when sizing feeders, branch circuits, and OCPD. But I can't find anything in the NEC about applying 125% as a demand factor in load calcs for sizing equipment like panels, transformers, etc.
This has recently become a question due to sizing step down transformers and panels feeding large electric vehicle charging installations. 625.42 says that we have to treat EV as continuous load. But does the 125% continuous load requirement apply to sizing transformers and panels?
Any code section references you can provide would be helpful.
Thank you.