Oishrock
Member
Do all raintight connectors need bond bushings? My buddy and I have been having a debate about Emt raintight connectors and whether they meet the definition of being bonded. The NEC 250.97 Bonding for Over 250 Volts For circuits of over 250 volts to ground, the electrical continuity of metal raceways and cables with metal sheaths that contain any conductor other than service conductors shall be ensured by one or more of the methods specified for services in 250.92(B), except for (B)(1). Exception: Where oversized, concentric, or eccentric knockouts are not encountered, or where a box or enclosure with concentric or eccentric knockouts is listed to provide areliable bonding connection, the following methods shall be permitted: (3) Fittings with shoulders that seat firmly against the box or cabinet, such as electrical metallic tubing connectors, flexible metal conduit connectors, and cable connectors, with one locknut on the inside of boxes and cabinets. The problem is the shoulder with a raintight connector doesn't fit against the box/cabinet due to the gasket/washer that is supposed to make it raintight.