vfd blowing up (Pete Benoit)
I recently finished a office warehouse for a large mech contractor.In the past 3 weeks 2 small honeywell NXL one hp drives have exploded



I have the same problem in a bioenergy plant and i can not solve the problem.
So i be grateful if enybady nows if he solved the problem.
 
vfd blowing up (Pete Benoit)
I recently finished a office warehouse for a large mech contractor.In the past 3 weeks 2 small honeywell NXL one hp drives have exploded



I have the same problem in a bioenergy plant and i can not solve the problem.
So i be grateful if enybady nows if he solved the problem.

The first place to contact with a problems like this is the manufacturer. If there are two people having a similar problem the odds are that there are more out there with the same problem. If nothing else the manufacturer will need feed-back from you so as to even start to correct any problems with their equipment.
 
Just had something like this happen at a local car wash. Turns out that there was an unidentified "stinger" leg, that they had hook the 120v motors too.
 