I stated the question incorrectly.
I have to run wire from house to barn and well. It will be a 200 amp circuit with aluminum wire 4/0 4/0 4/0 and #2 EGC.
I have some 350 MCM wire which I will use for the two hot wires. Since it is larger wire it will work even better and I assume that I can leave the other wires the same. Will this be OK with the inspector?
250.122(B) Increased in Size. Where ungrounded conductors are
increased in size from the minimum size that has sufficient
ampacity for the intended installation, wire-type equipment
grounding conductors, where installed, shall be increased in
size proportionately according to the circular mil area of
the ungrounded conductors
How much neutral current is expected? Can be smaller than 4/0 if neutral is well balanced and never sees much load. Can never be smaller than minimum required EGC though on a feeder or min SSBJ for service conductor.In order to lower the voltage drop, I am increasing my conductors from size 4/0. To 350 MCM. Is it OK to leave the neutral at 4/0 and leave the ground wire at number two. All the Wires are aluminum.
I stated the question incorrectly.
I have to run wire from house to barn and well. It will be a 200 amp circuit with aluminum wire 4/0 4/0 4/0 and #2 EGC.
I have some 350 MCM wire which I will use for the two hot wires. Since it is larger wire it will work even better and I assume that I can leave the other wires the same. Will this be OK with the inspector?
It is not a perfect rule either, it is the best they could come up with for a one size fits all type of rule. Some installations it makes sense, others it is overkill.Unfortunately, even if you are using larger conductor just because you have a spool of it around you still have to increase the EGC size. The idea is that the EGC is sized to the OCPD rating and the assumed conductor size that the OCPD would normally be paired with. Using a larger conductor reduces the resistance in the circuit which will increase the fault current the EGC has to carry and the EGC can act as a choke point for the ground fault current increasing the time it takes for the OCPD to operate. Using a larger EGC will account for this.
Expanding a little on what kewired said:
For what it is worth, the NEC would be perfectly happy with the ungrounded conductors not being oversized in the first place, which would make the trip time even worse.
Another argument is that the voltage divider effect before the OCPD trips will make the momentary voltage on grounded surfaces higher than it would be if the EGC is also oversized. But since it would be at least one half of the line voltage anyway, I do not see that as particularly important.
If you take as given that a size increase for VD will only be done if the VD would otherwise be more than 5%, then the need to upsize the EGC to maintain low trip time does make sense.
If you upsize to reduce 2% VD to 1% VD, then the motivation to upsize the EGC iscbmnot nearly as strong.
Sent from my XT1585 using Tapatalk
It is not a perfect rule either, it is the best they could come up with for a one size fits all type of rule. Some installations it makes sense, others it is overkill.
Some installations where conductor isn't "upsized" but is a long run, you will have much slower response of OCPD if there is a short circuit or ground fault even though you are in compliance with conductor sizing - resistance of conductor is going to be current limiting.
I will be installing:
350 MCM
350 MCM
4/0 NEUTRAL
#1 GROUNDING
ALL ALUMINUM IN 3 INCH PVC CONDUIT