MD88

Member
Hi there, here's my situation...

I'm designing the fire alarm system for a mill and there are a bunch of small (~5000 sq ft) buildings around, each with their own FACP. The entire system is monitored at a central location in the main mill, so I was wondering if I need to have an annunciator at each building? There's an FACP in the electrical room of each building, and each electrical room has a direct access door to outside.

Thanks
 

cadpoint

Senior Member
Location
Durham, NC
The code now states that the FACP or an Ann will be within 10' of the entrance.

Well the Pull station needs to be with-in fifeteen feet of the door.
I was told by an F/A tech that five feet was required for the Pull stations.

I have two differnt building on the same property (by deeding) with two different addresses and there's no interlink between building they both have a FACP. Your milage may vary...
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
The code now states that the FACP or an Ann will be within 10' of the entrance.

"THE" code? Which code? NFPA 72? IBC? IFC? Local? Blanket assertions aren't helpful.

A quick Google search reveals that a number of jurisdictions have adopted this as a guideline or "code" requirement, but it is by no means universal.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
NFPA-70 of the NEC

The only occurance of "annunciator" in the 2008 edition has to do with running a generator to failure.

The 2007 edition of NFPA 72 says:

"4.4.6.3* Annunciator Access and Location. All required annunciation means shall be readily accessible to responding personnel and shall be located as required by the authority having jurisdiction to facilitate an efficient response to the fire situation."

Still nothing about 10'.
 

wbalsam1

Senior Member
Location
Upper Jay, NY
I just came off your other post on inspectors adopting, I can only think "word-smith". :wink:

Yup. You got me! :smile: Blame it on years of trying to make sense of the NEC. I'm just pokin' at you anyways. There's just too few pita's left on this site....so, well you know. :D
 