zemingduan
Senior Member
- Location
- Philadelphia,PA
- Occupation
- Electrical Designer
Please see picture below. The reviewer gives us a comment says main over current device is required ahead of the taps. He didn't specify where do we need the main over current device. But IMO we don't need any extra over current device anywhere by code.(3 locations are marked out by 1,2,3 )

Some detailed questions:
1. At location 1. We don't need a tap box. We just need a junction box or maybe even a junction box is not needed, since there are 2 sets of service conductors coming in and one set feeds the 300 amps meter, another set feeds the rest of the equipment. Am I right?
2. At location 2. We don't need a main over current device for this bus conductor tapped from the service conductor. IMO, the bus conductor is service conductor rather than a tap conductor(even though it is tapped from service conductor). Conductor before the service disconnect means is service conductor according to the definition of service conductor in NEC 100. Thus we don't need to apply 240.21. Am I right?
3. At location 3. We do need a disconnect since conductor for panel EP is a tap conductor and over 25ft.
4. Is it a thumb up design to use a disconnect for this bus conductor, but it's not required by code?
I am a new graduated student and just working on electrical design for a year. I know you guys are awesome. First time posting, I am looking forward to your ideas. Thanks!

Some detailed questions:
1. At location 1. We don't need a tap box. We just need a junction box or maybe even a junction box is not needed, since there are 2 sets of service conductors coming in and one set feeds the 300 amps meter, another set feeds the rest of the equipment. Am I right?
2. At location 2. We don't need a main over current device for this bus conductor tapped from the service conductor. IMO, the bus conductor is service conductor rather than a tap conductor(even though it is tapped from service conductor). Conductor before the service disconnect means is service conductor according to the definition of service conductor in NEC 100. Thus we don't need to apply 240.21. Am I right?
3. At location 3. We do need a disconnect since conductor for panel EP is a tap conductor and over 25ft.
4. Is it a thumb up design to use a disconnect for this bus conductor, but it's not required by code?
I am a new graduated student and just working on electrical design for a year. I know you guys are awesome. First time posting, I am looking forward to your ideas. Thanks!