DragonElectric
Member
- Location
- New Jersey
- Occupation
- Engineer
I am working on my house that was built in 1940 and was flagged by the Home Inspector as not meeting code the Stove Hookup and the purchasers want it fixed.
At some point in time before I owned the home, there was a Subpanel (Ancient Square D QO, Main Lug, probably installed in the 1960s) installed dedicated to a Cooktop and Oven. The Oven was a plug in and wired to a 2 Pole breaker in the subpanel. The Cooktop was wired to a dedicated two pole breaker as well. When the Cooktop failed about a decade ago, I changed the oven and cooktop out to a traditional combined range. The current Stove is three wire with the Neutral and Ground bonded at the stove.
The Subpanel is fed from a Dedicated (2) Pole 60A Breaker in the Main Panel. The Main Panel was installed in 1989 (200A Cutler Hammer, CH) and has Inspection Sticker approving service from the township attached. The Subpanel is fed with an SE Cable (2 Hots and a Concentric Neutral), WITHOUT a EGC (Ground) or Ground bus.
My understanding was that prior to 1996, Stoves and Ranges were acceptable to be on a three wire circuit. What I don't know is if this same provision applied to a Subpanel dedicated to the stove and this would be grandfathered.
I understand that if I am installing a subpanel today that it needs a dedicated EGC and 4 Wires going to it... L1, L2, N, G and the Neutral and Ground bus are only bonded in one place.
What are my options here?
Option #1 - Tell them to pound sand. The current setup was approved multiple times in the past by the AHJ and is grandfathered and code is not retroactive. These buyers have been a nightmare so far (their contingency on their current home fell through once extending closing, their lawyer is real pushy and wants me to remediate any code issues from the inspection report or provide a 30K bond for them to handle! If I agree they will be going to town on the upgrades in the home, wiping out any profit).
Option #2 - Install an EGC back to the Main Panel or another accessible location? Would this be allowed as an exception to NEC 250 for an existing circuit without and EGC. I probably could find a path to route a #10 AWG EGC, but it will not follow the same route at the phase and neutral conductors due to accessibility.
Option #3 - Re-Pull a 4 Wire Service from Main Panel. This is not an easy task since the cables are buried in walls/ceilings. This is a multiple thousands of dollars fix and very intrusive.
Option #4 - Convert to gas! I say this jokingly but it would cost less money to buy a new gas range and extend the gas service from my heater the the range area then Option #3.
Thanks for any insight. I am always amazed at the level of knowledge here on this site.
At some point in time before I owned the home, there was a Subpanel (Ancient Square D QO, Main Lug, probably installed in the 1960s) installed dedicated to a Cooktop and Oven. The Oven was a plug in and wired to a 2 Pole breaker in the subpanel. The Cooktop was wired to a dedicated two pole breaker as well. When the Cooktop failed about a decade ago, I changed the oven and cooktop out to a traditional combined range. The current Stove is three wire with the Neutral and Ground bonded at the stove.
The Subpanel is fed from a Dedicated (2) Pole 60A Breaker in the Main Panel. The Main Panel was installed in 1989 (200A Cutler Hammer, CH) and has Inspection Sticker approving service from the township attached. The Subpanel is fed with an SE Cable (2 Hots and a Concentric Neutral), WITHOUT a EGC (Ground) or Ground bus.
My understanding was that prior to 1996, Stoves and Ranges were acceptable to be on a three wire circuit. What I don't know is if this same provision applied to a Subpanel dedicated to the stove and this would be grandfathered.
I understand that if I am installing a subpanel today that it needs a dedicated EGC and 4 Wires going to it... L1, L2, N, G and the Neutral and Ground bus are only bonded in one place.
What are my options here?
Option #1 - Tell them to pound sand. The current setup was approved multiple times in the past by the AHJ and is grandfathered and code is not retroactive. These buyers have been a nightmare so far (their contingency on their current home fell through once extending closing, their lawyer is real pushy and wants me to remediate any code issues from the inspection report or provide a 30K bond for them to handle! If I agree they will be going to town on the upgrades in the home, wiping out any profit).
Option #2 - Install an EGC back to the Main Panel or another accessible location? Would this be allowed as an exception to NEC 250 for an existing circuit without and EGC. I probably could find a path to route a #10 AWG EGC, but it will not follow the same route at the phase and neutral conductors due to accessibility.
Option #3 - Re-Pull a 4 Wire Service from Main Panel. This is not an easy task since the cables are buried in walls/ceilings. This is a multiple thousands of dollars fix and very intrusive.
Option #4 - Convert to gas! I say this jokingly but it would cost less money to buy a new gas range and extend the gas service from my heater the the range area then Option #3.
Thanks for any insight. I am always amazed at the level of knowledge here on this site.